in the nyc 1968 code, is a kitchen in a restaurant considered part of the F-4 occupancy so that there is no rating on the partition or is it considered the D-2 occupancy classification? It appears the D-2 would be for an industrial kitchen with no dining area where as a kitchen in a restaurant would be able to fall under the F-4 occupancy? thoughts? Clear distinction that can be found in the code would be greatly appreciated.
I did a restaurant a few years ago, using 1968 code, no separation was required per 1968 code section 27-339
Nonresidential kitchens need not be separated by fire separations from adjoining dining spaces, provided:
(1) The cooking equipment is vented directly to the outdoors, and
(2) 2 draft curtain of noncombustible material, at least twenty-four inches down from the ceiling, is provided to separate the cooking facilities from dining spaces, and
(3) Sprinkler heads constructed in accordance with the provisions of subchapter seventeen of this chapter, are provided on the cooking facilities side of the curtain, or any opening between the kitchen and dining space, located within twenty-four inches of the curtain or opening, and spaced not more than forty-eight inches on centers if the opening is more than sixty inches wide. When fire separations are provided double-action doors may be permitted.
Jan 29, 23 9:06 pm ·
·
Block this user
Are you sure you want to block this user and hide all related comments throughout the site?
Archinect
This is your first comment on Archinect. Your comment will be visible once approved.
1968 NYC code on kitchens
in the nyc 1968 code, is a kitchen in a restaurant considered part of the F-4 occupancy so that there is no rating on the partition or is it considered the D-2 occupancy classification? It appears the D-2 would be for an industrial kitchen with no dining area where as a kitchen in a restaurant would be able to fall under the F-4 occupancy? thoughts? Clear distinction that can be found in the code would be greatly appreciated.
I think your time machine is broken.
If only. Working in NYC is fun.
The infamous avocado appliance rule... we all suffered that one.
I did a restaurant a few years ago, using 1968 code, no separation was required per 1968 code section 27-339
(1) The cooking equipment is vented directly to the outdoors, and
(2) 2 draft curtain of noncombustible material, at least twenty-four inches down from the ceiling, is provided to separate the cooking facilities from dining spaces, and
(3) Sprinkler heads constructed in accordance with the provisions of subchapter seventeen of this chapter, are provided on the cooking facilities side of the curtain, or any opening between the kitchen and dining space, located within twenty-four inches of the curtain or opening, and spaced not more than forty-eight inches on centers if the opening is more than sixty inches wide. When fire separations are provided double-action doors may be permitted.