What is a class C roof???? It is for an A3 occupancy group in LA
Thanks
Mar 22, 07 2:17 pm
treekiller
think it has to do with flammability in the fire code- ie wood shakes versus tile
Mar 22, 07 2:32 pm  ·
vado retro
Q: What do the fire-resistance classifications A, B and C mean in reference to roofing materials?
A: Fire-resistance classifications measure roof assemblies' relative resistances to external fire exposures. Building codes cite these classifications to establish minimum fire-resistance requirements for different types of buildings and structures. To determine its classification, a product or roof assembly usually must be independently tested using the fire-resistance capacity tests stated in a building code.
ANSI/UL 790, "Tests for Fire Resistance of Roof Covering Materials," and ASTM E 108, "Standard Test Methods for Fire Tests of Roof Coverings," are the fire-resistance capacity tests used to determine a product's or roof assembly's classification. Both standards essentially use the same test methods; therefore, products and roof assemblies successfully tested in accordance with either standard result in Class A, B or C ratings.
Each standard includes an intermittent-flame exposure test, spread-of-flame test, burning-brand test, flying-brand test and rain test. The test or combination of tests required to determine classification varies for each product or roof assembly.
For example, to determine the fire-resistance classification of a product or roof system that is restricted for use on noncombustible decks (e.g., steel, concrete, gypsum), only the spread-of-flame test is required. However, a product or roof system that can be used on a combustible deck (e.g., wood) must be subjected to the spread-of-flame test, as well as the intermittent-flame and burning-brand tests.
The flying-brand test only is required when there is a possibility that pieces of a product or roof assembly (e.g., a wood roof covering over spaced sheathing) could fall into a building and add to combustion on the floor below. Rain tests are required when the fire-retardant characteristics of a product or roof assembly, such as a coated, smooth-surfaced roof system, could be affected adversely by water.
Fire-resistance classifications A, B and C are intended to represent different levels of fire-resistance performance. They are defined by ANSI/UL 790 and ASTM E 108 as follows:
Class A roof coverings are not readily flammable, are effective against severe fire exposures, and do not carry or communicate (i.e., spread) fire.
Class B roof coverings are not readily flammable, are effective against moderate fire exposures, and do not readily carry or communicate fire.
Class C roof coverings are not readily flammable, are effective against light fire exposures, and do not readily carry or communicate fire.
A product or roof assembly is assigned a classification based on the fire-resistance tests it completes successfully. For example, to determine a Class A rating with the burning-brand test, a 12- by 12- by 2 1/4-inch (305- by 305- by 55-mm) gridded configuration consisting of three tiers of 12 12-inch- (305-mm-) long wood strips is placed on top of a test sample while air is forced over the brand. The brand is allowed to burn—not longer than 1 1/2 hours—until it self-extinguishes or the roof assembly fails.
The same process is used to determine a Class B rating, but a 6- by 6- by 2 1/4-inch (150- by 150- by 55-mm) gridded configuration consisting of three tiers of six 6-inch- (150-mm-) long wood strips is used instead.
For a Class C rating, a test sample is subjected to a 1 1/2- by 1 1/2- by 25/32-inch (38- by 38- by 20-mm) block of wood with one saw kerf on the wood block's top and bottom faces.
Fire-resistance classifications also are used by model building codes. Uniform Building Code, 1997 Edition, prescribes minimum roof classifications in Table 15-A, "Minimum Roof Classes," based on occupancy and construction types. Roof classifications are A, B, C, noncombustible or nonrated; Class A, B and C roofs are tested in accordance with ANSI/UL 790.
The BOCA [Building Officials and Code Administrators International Inc.] National Building Code/1999 describes roof classifications in Section 1506, "Fire Classification," and establishes minimum roof classifications based on construction type. Class A, B and C roofs are tested in accordance with ASTM E 108.
Standard Building Code, 1999 Edition, describes roof classifications in Section 1505, "Fire Classification," and Class A, B and C roofs are tested in accordance with ASTM E 108 or ANSI/UL 790.
Class A, B and C ratings are for external fire resistance of a product or roof assembly—they have no direct bearing on hourly fire ratings. Hourly fire ratings are for a roof/ceiling assembly's integrity when a fire occurs inside a building.
Essentially, fire-resistance classifications are required for all products or roof assemblies used in commercial and residential buildings. A roofing contractor should be aware of model building codes' minimum requirements when not using Class A products or roof assemblies.
Each month in this column, one of NRCA's technical services staff members will answer readers' technical questions. If you have a specific question you would like answered in this column, send it to Professional Roofing magazine, 10255 W. Higgins Road, Suite 600, Rosemont, IL 60018-5607; or fax (847) 299-1183.
Mar 22, 07 3:15 pm  ·
el jeffe
if it applies, ask your client to check with their insurance company to see if they get a break by having an upgraded class (assuming B or C is code min).