I have been looking through the 2009 IBC all day and cannot find how many enclosed fire stairs are needed for a building. I was told that if your building is 2 stories that you only need one closed stair and can have one open stair. Can someone please help me I need to know ASAP, thank you!
IBC Egress Code Help
I have been looking through the 2009 IBC all day and cannot find how many enclosed fire stairs are needed for a building. I was told that if your building is 2 stories that you only need one closed stair and can have one open stair. Can someone please help me I need to know ASAP, thank you!
What is your occuppancy group and count?
http://publicecodes.cyberregs.com/icod/ibc/2009/icod_ibc_2009_10_sec021.htm
My occupancy is A-3 and my load is about 450 people for the whole building. So if I'm reading the chart right I need two?
Yes.... Also for assembly you can subtract the accessory spaces due to the clause in the code related to non simultaneous occupancy
ok thank you very much for your help!
no problem... the only question I have is... how on Earth didn't you see that chart after a day of searching in the code book?